SmurfOnABoat 05-07-2009 05:04 PM

Automatic Halon system recirtification times and others???
 
Just wondering how long between certifications for automatic Halon systems is, and how to tell if your tank is still charged or not.

On my auto halon in the engine compartment, there is no dial indicating charge. When I turn the key on, the dash light for the Halon system goes green, and says ok.

Thanks!

PS. And yes it is a Halon system, says right on the tank.

MrCIG 05-07-2009 05:17 PM

They are supposed to be check once a year. The only way to check them is to weigh the unit, the gross weight should be marked on the cylinder. If it does not weigh what is marked, it is no good. A local Fire Extinguisher company can certify it for you.

Mark

SmurfOnABoat 05-07-2009 09:25 PM

And if it is outdated, can it be filled and have the tank certified from the company, or do you just get new ones?

FREEZE FRAME VIDEO 05-08-2009 05:51 AM

I Called Fire Boy About Mine They Said They Do Not Refill Or Check This Units With Halon Any More. The gauge says in the good and also weigh it it and its good to go, freeze frame
http://i314.photobucket.com/albums/l...d/IMG_9851.jpg

Wobble 05-08-2009 12:02 PM

I have dual halon units and have been told I was good as long as the light was green. I have wondered if that was sufficient though.

MrCIG 05-09-2009 07:38 AM


Originally Posted by Wobble (Post 2861718)
I have dual halon units and have been told I was good as long as the light was green. I have wondered if that was sufficient though.

The problem with dual Halon system unless they are tied together and each one is sized to put out the fire. It will not put the fire out. THe chance of both systems fusing the head at the same time is slim.

The coast guard up here in Lake Michigan wrote warnings to a couple friends of mine because they didn't have thier units tagged.

Reading the guage is not enough nor is looking at the light. Guages stick and so do pressure switches. The unit must be weighed.

Because of DOT standards no manufacturer that I am aware of will refill a discharged unit.

Mark

SmurfOnABoat 05-09-2009 08:28 AM

Where is a good place to buy a replacement, automatic halon unit?

Wobble 05-11-2009 09:45 AM


Originally Posted by MrCIG (Post 2862248)
The problem with dual Halon system unless they are tied together and each one is sized to put out the fire. It will not put the fire out. THe chance of both systems fusing the head at the same time is slim.

The coast guard up here in Lake Michigan wrote warnings to a couple friends of mine because they didn't have thier units tagged.

Reading the guage is not enough nor is looking at the light. Guages stick and so do pressure switches. The unit must be weighed.

Because of DOT standards no manufacturer that I am aware of will refill a discharged unit.

Mark

They are both the correct size to extinguish a fire in that space. The theory was that one would do the job and the other if it re-ignited. The pressure circuits are wired in series so if either one fails the light will not illuminate.