04-18-2003, 01:07 PM
|
#1
|
|
Registered
Join Date: Mar 2001
Location: ohio
Posts: 2,560
1988 Cruisers 2800 Rogue
|
Question for Air Cond. techs
I am installing an old ac unit in my boat. Its a split system and I want to air pressure check the evaporator before I finish the lines and have it charged. What pressure should I use?
|
|
|
04-18-2003, 01:27 PM
|
#2
|
|
Platinum Member
 Platinum Member
Join Date: Sep 2001
Location: tn
Posts: 5,238
1991 F311SR1
|
R12 auto systems see as much as 250 psi on the condensing side. The evap rarely runs over 40 when in operation, but will see around 70 when the compressor is off and the system has equalized out.
Marine systems are designed for a "reverse cycle" option, which means that the pressures reverse in Heat mode. I'd expect an R22 marine system (or a 134a one) to see 160 regularly on both sides (if reverse cycle).
__________________
I see London, I see France...
|
|
|
04-18-2003, 01:37 PM
|
#3
|
|
Registered
Join Date: Jan 2003
Location: Stafford Va.
Posts: 2,718
98 NORTECH 5000V
|
your going to want to put a vacuum on it and suck it down to get all the moister out and most vacuums will have a Gage so you can see if it is air tight. If it's a R12 system change it over to R134 now it's a hell of a lot cheaper. If you use air psi to test the system you are just pumping more moister in and you want to get it all out. Make sure you check to see if it need's oil to so you can put it in when you charge it up.
|
|
|
04-18-2003, 01:51 PM
|
#4
|
|
Registered
Join Date: Mar 2001
Location: ohio
Posts: 2,560
1988 Cruisers 2800 Rogue
|
Thanks, this is a reverse cycle r22 system so ill check it at 160. My buddy has the vacuum pump and guages and will help me charge it when Im ready. I wanted to check the evaporator now since it will be buried very soon.
|
|
|
04-18-2003, 02:29 PM
|
#5
|
|
Gone Fishin'
 Charter Member
Join Date: Nov 2000
Location: Grand Rapids/Holland/Grand Haven
Posts: 7,408
1988 Tracker Pro 17, 40 hp Mariner.....1972 Glastron GT 140, Merc 50 power!!!
|
Like I told you the other night Tom (when I was stoned on pain killers), you put A/C in your boat and you will SUCK!!!! LOL!!
Just jealouse.
__________________
[b]M Go Blue.......Gator boots, gator luggage, gator purses... all at cut rate deals!!!!
|
|
|
04-18-2003, 04:46 PM
|
#6
|
|
Member #9
 Charter Member
Join Date: Oct 2000
Location: Pewaukee, WI
Posts: 4,136
|
Lapse is right, you want to pull the system into a vacuum NOT pressurize it. Pulling it into a vacuum not only tells you if it is sealed but also removes all the moisture from the system. Let the system sit for a while in a vacuum, verify it is not leaking then charge it while the gauges are still on. You will end up with a moisture free, leak proof system.
__________________
Member of the Liquid Jungle
|
|
|
04-18-2003, 05:27 PM
|
#7
|
|
VIP Member
VIP Member
Join Date: Oct 2002
Location: CT
Posts: 749
1987 Sonic 30 SS
|
Use dry nitrogen to pressurize system. I've seen new installs hold a vacuum, and as soon as pressure was added leak!. If your buddy has guages and a pump he'll probably have a nitrogen cyl. too.
|
|
|
04-18-2003, 09:29 PM
|
#8
|
|
Registered
Join Date: Jan 2002
Location: ALTO, MI
Posts: 2,516
1992--34 SCARAB
|
I agree with SONIC. USE NITROGEN and pressure test it to 100 psi and soap solution the joints for leaks.
|
|
|
04-18-2003, 09:39 PM
|
#9
|
|
Registered
Join Date: Mar 2001
Location: ohio
Posts: 2,560
1988 Cruisers 2800 Rogue
|
The evaporator has been open to air for months if not years. I dont see where some clean, dry air is gonna make things any worse than they are already. Nitrogen will set me back another week or more and the system wont be pulled down and charged until june or july. I have half the boat interior torn apart for the installation and it needs to be put back together soon. The compressor and condensor are hiding in the engine compartment.
|
|
|
04-29-2003, 10:57 PM
|
#10
|
|
Registered
Join Date: Jan 2002
Location: ALTO, MI
Posts: 2,516
1992--34 SCARAB
|
The nitrogen will help with the drying process. Also replace the freon filter drier. It will be a bulge in the liquid line going from the condenser to the evaporator. It may be inside the condenser assembly. If it has one it MUST be replaced.
|
|
|