Question OT: What size wire for Hot Tub?

I need help.

What size direct burial 220v wire do I need for a 30' run for my hot tub? I'm running a 30 amp breaker. Thanks in advance for any help.
NW_Jim is offline  
Reply With Quote
Old 07-01-2002, 07:00 PM
  #2
Registered
 
Shorty's Avatar
 
Join Date: Apr 2001
Location: LOTO / Overland Park, KS
My Boats: 1999 Mach1 290
Posts: 375
Default

Don't forget the ground spike... BZZZZZZZZZZZZ!!!
Shorty is offline  
Reply With Quote
Old 07-01-2002, 07:10 PM
  #3
Registered
 
thunderdan's Avatar
 
Join Date: Oct 2000
Location: medford, nj usa
My Boats: 37 Active Thunder
Posts: 2,185
Default

I would use 8-3 romex wire. Make sure you use a quick disconnect out at the building before it goes into your house. Are you sure about 30 amp, that seems a bit small?

Dan
thunderdan is offline  
Reply With Quote
Old 07-01-2002, 07:12 PM
  #4
Registered
 
Join Date: Apr 2001
Location: Glens Falls, NY
My Boats: 1999 36' cutdown Skater
Posts: 131
Default

30 amp is # 10 gage copper. Is that what the tub draws or the recommended breaker? Anyway # 10 is the right choice. 4 wire mc is the best for a tub ...ie red black white green or bare and the jacket is grounded.

Ted
Ted Zoli is offline  
Reply With Quote
Old 07-01-2002, 07:48 PM
  #5
Registered
Thread Starter
 
NW_Jim's Avatar
 
Join Date: Dec 2000
Location: NW USA
My Boats: 1990 35' Fountain
Posts: 797
Default

OK, I checked inside the tub. It says 40 amp breaker and #6 wire. This is going into my shop subpanel. The ground spike is right next to the tub. Does # 6 sound right for a 40 amp breaker and 30 feet?
NW_Jim is offline  
Reply With Quote
Old 07-01-2002, 07:50 PM
  #6
Registered
 
Turbojack's Avatar
 
Join Date: Sep 2001
Location: Houston, TX, USA
My Boats: 2003 Eliminator 30' Daytona
Posts: 2,285
Default

Aaaa, multi answers to simple question. If hot tub needs 30A 220v then #10cu is correct wire size. Will need 4 wires, 2 phase conductors ( red & black), 1 neutral (white), & 1 ground (bare). Wire type for direct burial is UF so you would need 10/4 UF cable. I do not know if this is made. I would not use romex direct burial. If I was doing I would run a PVC pipe & put wire in pipe. Then buy a GFI 30A double pole breaker in panel to feed this. GFI breakers are not cheap but neither is a life.

If hot tub requires 40A then #8 cu. wire
If hot tub requiers 50A then #6 cu. wire
Turbojack is offline  
Reply With Quote
Old 07-01-2002, 08:09 PM
  #7
Registered
 
Join Date: Apr 2001
Location: Glens Falls, NY
My Boats: 1999 36' cutdown Skater
Posts: 131
Default

Sorry...missed the "direct burial." Do not use mc!

Type UF (underground feeder) or USE (underground service entrance) will both do fine...UF easier to work with. All of the sizes you have been given are exactly correct IMHO. Pick an ampacity and go. Ground fault breaker a must.

Ted
Ted Zoli is offline  
Reply With Quote
Old 07-01-2002, 09:19 PM
  #8
Registered
Thread Starter
 
NW_Jim's Avatar
 
Join Date: Dec 2000
Location: NW USA
My Boats: 1990 35' Fountain
Posts: 797
Default

Ok, Thanks for all the help. The inside cover of the wooden enclosure says 50 amp so that is what I went with. Got #6 UF and a 50 amp breaker. I also ran a separate ground wire to the spike since it was closer. Thanks for all the help guys. Now all I need is some neked women.
NW_Jim is offline  
Reply With Quote
Old 07-01-2002, 09:26 PM
  #9
Registered
 
PhantomChaos's Avatar
 
Join Date: Dec 2000
Location: Bell Canyon, CA
My Boats: Formula FASTech 382 Sunseeker Apache 45
Posts: 12,756
Default

Jim-

Make sure you have a normal breaker at the box, AND a GFI breaker (required by code) as near to the spa as possible in a seperate breaker box. Looks like you've been recommended the correct guage wire for 50A 220V, four wire. Good luck in the spa (I meant with the spa).
PhantomChaos is offline  
Reply With Quote
Old 07-01-2002, 11:46 PM
  #10
Chevy-Harley fan
Charter Member
 
gmhdfan's Avatar
 
Join Date: Mar 2001
Location: Orlando, Fl. USA
Posts: 1,385
Default

I have about a 80 foot run from my service to the spa area. How many feet can you go before you have to use bigger wire?
gmhdfan is offline  
Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 04:16 PM.


Copyright 2011 OffShoreOnly. All rights reserved.