I just installed air in my 35 Sonic. I'm having a problem where the aluminum fins on the retun side of the unit are freezing solid with ice after a couple hours of running.

Does anyone know what would cause this? a buddy of mine re-charged the unit to make shure it was good on freon. he also verified i had enough return flow getting to the unit.

any ideas??
HiPerf2000 is offline  
Reply
Old 07-31-2005 | 07:13 AM
  #2  
NASTY HABIT's Avatar
Registered
 
Joined: Feb 2002
Posts: 1,956
Likes: 0
From: Orlando
Default Re: Air Conditioner question ???

could be a number of things....low charge , low airflow(restricted by something or dirty) , low return temp, or a combination of the above....after a few hours what is the temp of the cabin?

why did he check the charge?

Last edited by NASTY HABIT; 07-31-2005 at 07:15 AM.
NASTY HABIT is offline  
Reply
Old 07-31-2005 | 08:54 AM
  #3  
Strip Poker 388's Avatar
Rob
20 Year Member
VIP Member
 
Joined: Aug 2001
Posts: 21,637
Likes: 12
From: Ms
Default Re: Air Conditioner question ???

Maybe a recycling switch. letting the the compressor not cut off making the condenser freeze up?
__________________
.

The Only Time You Have To Much Ammo Is When Your Swimming Or On Fire.
Strip Poker 388 is offline  
Reply
Old 07-31-2005 | 09:25 AM
  #4  
HiPerf2000's Avatar
Thread Starter
Registered
 
Joined: Oct 2000
Posts: 4,082
Likes: 2
From: N.E.
Default Re: Air Conditioner question ???

Originally Posted by NASTY HABIT
could be a number of things....low charge , low airflow(restricted by something or dirty) , low return temp, or a combination of the above....after a few hours what is the temp of the cabin?

why did he check the charge?
last time i checked the digital thermostat before it froze, the temp was 77 (have it set for 73). The reason why we checked the charge was to rule out the low charge theory. And It was a bit low due to a small leak in a schrader valve. (this is a used unit). We put some pipe sealer around the cap and it seemed to hold. he left the gauges on there for 15 minutes and closed the hatch where it is mounted....and the pressure never dropped. So he said my return supply must be good or he would have seen a pressure drop after he closed the hatch.
HiPerf2000 is offline  
Reply
Old 07-31-2005 | 10:25 AM
  #5  
nautiintention's Avatar
Registered
 
Joined: Mar 2004
Posts: 26
Likes: 0
From: Pasadena, MD
Default Re: Air Conditioner question ???

What kind of refrigerant is this system using and what were the pressures (both high and low side)?
nautiintention is offline  
Reply
Old 07-31-2005 | 11:03 AM
  #6  
HiPerf2000's Avatar
Thread Starter
Registered
 
Joined: Oct 2000
Posts: 4,082
Likes: 2
From: N.E.
Default Re: Air Conditioner question ???

the refrigerant is R22. I forget what the high side was, but the low side was 55 and he charged it up to 68. This is a 7k btu Marine Air unit.
HiPerf2000 is offline  
Reply
Old 07-31-2005 | 02:12 PM
  #7  
Registered
 
Joined: Oct 2000
Posts: 1,238
Likes: 0
Default Re: Air Conditioner question ???

Your talking like this is a split system.....or is it a package unit.
have any pics?

Last edited by enticer; 07-31-2005 at 02:27 PM.
enticer is offline  
Reply
Old 07-31-2005 | 07:52 PM
  #8  
HiPerf2000's Avatar
Thread Starter
Registered
 
Joined: Oct 2000
Posts: 4,082
Likes: 2
From: N.E.
Default Re: Air Conditioner question ???

Here is the website for the system.....

http://www.marineair.com/pdfs/vr.pdf
HiPerf2000 is offline  
Reply
Old 08-01-2005 | 08:28 AM
  #9  
Registered
 
Joined: Jan 2001
Posts: 1,658
Likes: 0
From: ST. Louis, MO, USA
Default Re: Air Conditioner question ???

Usually restricted air flow. Either clogged with dust/debris on the intake or kinked hose on the outlet. Also check to see if the fan is running at high speed.
Gary
Gary Anderson is offline  
Reply
Old 08-07-2005 | 09:39 AM
  #10  
nautiintention's Avatar
Registered
 
Joined: Mar 2004
Posts: 26
Likes: 0
From: Pasadena, MD
Default Re: Air Conditioner question ???

Sounds kind of odd to have the evaporator freeze up with a suction pressure of 68#. A 68# suction gives you a 40 degree evaporator coil. I can understand the 55# freezing up, that would be a 30 degree coil and moisture in the air would instantly freeze to the coil. Your suction pressure is dropping down below 58# for some reason. Are you sure that you do not have a refrigerant leak and you have lost some refrigerant again. How long does it run before it starts to freeze up. Does the cabin ever start to cool down?