So I bought a "new to me" boat and took delivery last Monday. It's at a marina on a lift. I go to plug in the shore power and after about 10-15 seconds the breaker (on marina side) pops. I can't figure it out...
Boat is a 2006 Formula 330SS with 496's, Generator, 3 new batteries, and looks to be unmolested in terms of wiring.
A few things that I did try...
I pulled off the boat receptacle and cleaned all the contacts
I also tried replacing the receptacle with a new one (when that didn't work I returned it and re-installed the old one)
Tried a different cord
Plugged into several different outlets on different breakers with the same results
The way it is wired is from the receptacle to a main breaker, then to the panel. If I turn off the main breaker and plug in it won’t pop. If I turn off the main at the panel (actually everything is off) and turn on the main breaker it pops. Mind you it takes about 15 seconds for it to pop and in the 15 seconds if I turn on the panel main the voltage comes up till it pops.
I'm at a loss, anybody have any ideas? Please feel free to ask questions.
Thanks
Aaron
alindquist is offline  
Old 08-18-2014, 08:05 PM
  #2  
Registered
 
Join Date: Dec 2006
Location: Toronto, Ontario
Posts: 3,194
Received 25 Likes on 14 Posts
Default

I have heard about other formulas having this issue. Do a quick search, I think it was due to a built in GFI in the boat, and a second on the dock. There should be a few threads about this.
Perlmudder is offline  
Old 08-18-2014, 08:14 PM
  #3  
Registered
 
Join Date: Dec 2006
Location: Toronto, Ontario
Posts: 3,194
Received 25 Likes on 14 Posts
Default

found it
http://www.offshoreonly.com/forums/g...pped-help.html
Perlmudder is offline  
Old 08-18-2014, 08:28 PM
  #4  
Registered
Thread Starter
 
Join Date: Mar 2006
Location: Navarre, FL
Posts: 409
Likes: 0
Received 1 Like on 1 Post
Default

Perlmudder - Thanks for the link... That was very helpful...
alindquist is offline  
Old 08-18-2014, 09:54 PM
  #5  
VIP Member
VIP Member
 
VoodooRob's Avatar
 
Join Date: Jul 2011
Location: Cleveland Ohio
Posts: 1,993
Received 46 Likes on 23 Posts
Default

I ran into this also. I carry a 3 prong to 2 prong conversion, problem fixed. I have only run into an issue at Lake Cumberland and at my home before I put in a dedicated line.
VoodooRob is offline  
Old 08-19-2014, 06:18 AM
  #6  
Registered
Thread Starter
 
Join Date: Mar 2006
Location: Navarre, FL
Posts: 409
Likes: 0
Received 1 Like on 1 Post
Default

So I dug around for hours last night reading posts and it turns out that I'm not alone and it is not exclusive to Formulas. It turns out that is it the Galvanic Isolator Monitoring System. Not the Galvanic Isolator it's self (that can still function). Apparently all I have to do is remove the fuse to the Monitor and that should fix my problem. I'll be down at the boat today and I'll let you guys know if this fixes it.
alindquist is offline  
Old 08-19-2014, 01:00 PM
  #7  
Registered
Thread Starter
 
Join Date: Mar 2006
Location: Navarre, FL
Posts: 409
Likes: 0
Received 1 Like on 1 Post
Default

Problem fixed... It was the monitoring system for the galvanic isolator. Pulled the fuses that run from the monitoring box to the AC panel, plugged in the boat and everything came online.
It is my understanding from reading another thread (link below) that when that system fires up it runs a check and puts some amount of voltage, or amperage, or something, to the ground which in turns pops the breaker... Anyways it's not the perfect fix, my galvanic isolator is working however the little test panel in the cabin does not run. I'm not sure there is a fix for that, I'm going to call ProMariner and see if they have anything.

Thanks for all the help guys.... Here is a link that thread again in case anybody else has the same issue.
http://www.regalownersforum.com/foru...P+GFI+Tripping
alindquist is offline  

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



Contact Us - Archive - Advertising - Cookie Policy - Privacy Statement - Terms of Service

Copyright © 2024 MH Sub I, LLC dba Internet Brands. All rights reserved. Use of this site indicates your consent to the Terms of Use.